1/5/2011 10:20 AM | |
Joined: 6/7/2010 Last visit: 7/9/2024 Posts: 571 Rating:
Dear All, I am using 6ES7331-7PF11-0AB0 Analog input module for Detect the oil temperature by using thermocouple.I have refered the attached document for connection, in that I have some dought, In that module ( 7,8 ),( 9,10 ),( 11,12 ),( 13,14 ) pin we will connect the thermocouple, but in 27 , 28,35,36,37 & 38 ( It is shown as varing ) pin is for what? Second one is , how to read the temperature in the PLC.I am using 840D,PCU50+S7 300.
AttachmentAnalog Input Unit.pdf (290 Downloads) |
Regards, |
1/6/2011 9:48 AM | |
Posts: 45 Rating:
Hi Muthamiz, To read the thermocouple value; you have to read the raw value of the thermocouple then divide it over 10. Good Luck, |
1/6/2011 10:00 AM | |
Posts: 45 Rating:
Attached a portion from S7-300 Module Specifications manual for what you are asking for.
AttachmentRepresentation of the analog values of thermocouples.pdf (301 Downloads) |
1/6/2011 10:05 AM | |
Joined: 3/21/2006 Last visit: 2/10/2025 Posts: 10239 Rating:
No, you can connect 8 termocouples.
How to read in PLC look at How and for which analog measurements can you use the function FC105 "SCALE" to convert the integer values (INT) into real number values? Best regards, Hristo Mihalev |
2 thankful Users |
2/19/2011 3:39 AM | |
Hi, While configure the Analog module ,wether we need to enter any information of thermocouple or any thing else.i have attached the photo of the screen .i am going to use 4 thermocouple. AttachmentNew Microsoft Office Word Document.zip (246 Downloads) |
Regards, |