11/3/2009 3:35 PM | |
Joined: 8/25/2005 Last visit: 7/5/2024 Posts: 1161 Rating:
|
Hello Corb, you dont have to configure the repeater with the MLFB 6ES7972-0AA01-0XA0 within your hardware configuration. It is part of your network. The repeater with the MLFB 6ES7972-0AB01-0XA0 could be configured as a DP-Slave if you want to get diagnstic data about your network within your PLC. This is why you have to configure it within your hardware configuration. Best regards Sabine |
Last edited by: Hulzhex at: 11/3/2009 3:36 PMWizard was faster than I was :-) |
|
This contribution was helpful to
2 thankful Users |
11/3/2009 4:28 PM | |
Posts: 12 Rating:
|
Thank u everybody |
4/20/2012 4:33 PM | |
Posts: 2 Rating:
|
does that mean that i dont need to set it on hw config or net pro? because i cant find6ES7 972-0AA01-0XA0 on the hw catalog of the step 7 |
4/20/2012 6:05 PM | |
Posts: 8946 Rating:
|
But it is a good idea to mark the repeater in the network - configuration! |
4/20/2012 7:27 PM | |
Posts: 2 Rating:
|
thank you very much guys 4 the help.... |