3/2/2020 10:11 PM | |
Joined: 1/25/2019 Last visit: 5/7/2023 Posts: 12 Rating: (0) |
I have a program with safety blocks how can I convert this blocks from safety blocks to standard blocks |
3/2/2020 11:40 PM | |
Joined: 9/27/2006 Last visit: 9/25/2024 Posts: 12283 Rating: (2685)
|
Hello mnz; I believe the only way to do this would be reprogramming the blocks in your standard program yourself. In any case, if all you are considering is conversion of the Safety blocks (F-B;locks) and not the surrounding Safety engineering, the available F-Blocks that you could convert are very few: timers, counters, pulse inputs, math and logic functions, CPU-CPU communication... All the other F-Blocks are channel drivers for F-IO, F-runtime and shutdown group management, IO voting blocks,,, that you cannot use in a standard program. So conversion of the logic into standard blocks should not be a difficult task. See the following screenshot, listing ll available F-Blocks for the F-System software. This was taken from the Simatic Safety Engineering system manual: https://support.industry.siemens.com/cs/ww/en/view/12490443 Hope this helps, Daniel Chartier |
This contribution was helpful to1 thankful Users |
3/3/2020 4:25 PM | |
Joined: 1/25/2019 Last visit: 5/7/2023 Posts: 12 Rating: (0) |
Thank you very much
|