10/17/2012 9:43 PM | |
Joined: 9/27/2006 Last visit: 9/16/2024 Posts: 12282 Rating: (2684)
|
Hello R&H Co.; If you look at the Successor Product tab for the 6ES7312-5CA00-0AB0, you will find the 6ES7312-5CA02-0AB0. so they are considered direct replacements andyour new CPU moduleshould run with the uploaded program (if the upload was complete). https://support.automation.siemens.com/WW/llisapi.dll?func=cslib.csinfo&lang=en&objid=4067768&caller=view What do the LEDs show on the CPU after you download the program? Have you tried a Master Reset (with the front key of the CPOU, max. right 2 seconds, release, right 10 seconds until the LEDs stop flashing)? Can you go online with the new CPU? have you tried opening the diagnostic buffer to see what is not acceptable in the downloaded programfor the CPU? Hope this helps, Daniel Chartier |
10/18/2012 5:09 PM | |
Joined: 4/22/2010 Last visit: 5/3/2024 Posts: 5697 Rating: (715)
|
Hello, The ??? are there because your hardwarecatalog is not up to date, try update hardware catalog. How do you update the STEP 7 hardware catalog in STEP 7 V5.2 onwards? What version off Step7 you have there? To change CPU, you have only to right-click on CPU (in hardware config)and select replace, then choose the New CPU in the list, save and compile and download hardware and program in new CPU . Regards, Marcjan |
Last edited by: Marcjan at: 10/18/2012 5:33 PMinserted link Problem solved? |
|