7/11/2014 6:28 AM | |
Joined: 11/21/2007 Last visit: 3/31/2025 Posts: 2326 Rating:
|
HelloKRS2008104567 A CP 341 can be used with its integrated Communication Drivers or Special "Loadable" Drivers. CP-341 has several integrated Drivers e.g. ASCII , 3964R , etc . In case these drivers have been used, then you can just remove the existing CP-341 and plug in the new CP-341. However several loadable drivers are also available for CP-341 e.g. In case of loadable drivers, after replacement of the CP341, the driver has to be downloaded to the module. Pl follow the following procedure : Remove the existing module. Remove the Blue Colored Hardware Dongle at the back of the old module Plug the dongle into the new module. Install the new module into the Rack. Download the Relevent Driver from the corresponding link provided above ( Pl check the version ) Download the Driver to the CP-341 ( Procedure provided in the manuals available on the above links ) Hope this helps Cheers Navnag |
There is no such thing as the last bug in a program |
|
This contribution was helpful to
2 thankful Users |
7/11/2014 9:06 AM | |
Posts: 24 Rating:
|
PLC Firmware Version: V2.0.11 CP341 Old Module Firmware Version: V1.0.2 CP341 Replacement Module Firmware Version: V2.1.1 Thank you. Regards. |
7/11/2014 9:45 AM | |
Joined: 11/21/2007 Last visit: 3/31/2025 Posts: 2326 Rating:
|
HelloKRS2008104567 If there is no Dongle it should be 100% plug-and-play, right?- Absolutely right for compatible Firmware Versions. In your case Old Firmware and new Firmware do seem to have an issue. Pl Check : As per this Update : The new firmware version V2.1.0 optimizes the data throughput of the CP341-V2: To be able to utilize the higher performance you require the "Configuration Package for Point to Point Communication“ with version V5.1 incl. SP11 (see entry ID 27013524). The parameterization data for the CP341-V2 (FW version V2.1.0 and higher) must be newly generated with PtP-Param V5.1.11 for this purpose. Therefore you should regenerate the PtP Parameters for this CP341 and download to the CPU. Alternatively you can downgrade the firmware version ( I would however not recommend this ) Hope this helps Cheers Navnag |
There is no such thing as the last bug in a program |
|
7/11/2014 10:07 AM | |
Posts: 24 Rating:
|
I agree. I am currently downloading this drivers. CP PtP parametrization software http://support.automation.siemens.com/WW/llisapi.dll/csfetch/27013524/Setup_PtP_V5114.exe?func=cslib.csFetch&nodeid=81303630 ) Modbus slave drivers http://support.automation.siemens.com/WW/llisapi.dll/csfetch/27774276/Modbus-Slave319.exe?func=cslib.csFetch&nodeid=64128597) . But the mystery is, how come the previous replacement worked simply as plug-and-play while the later does not. Anyway THANK YOU VERY MUCH! for your assistance. Regards. |
This contribution was helpful to
1 thankful Users |
7/15/2014 10:08 AM | |
Posts: 24 Rating:
|
No the modules does not have a Dongle. IsPtP param V5.11 SP 14 ok to use for this firmware? This version was suggested by our OEM. Thanks. |