4/25/2012 10:04 AM | |
Joined: 12/1/2009 Last visit: 6/7/2024 Posts: 672 Rating:
Dear boazeventall , can you kindly make a screenshot of your currentlogic and post it here. We will correct it as per your requirement. Regards. |
Give us your feedback and show us your respect! |
4/25/2012 10:08 AM | |
Posts: 131 Rating:
look at the picture |
4/25/2012 10:20 AM | |
Joined: 4/20/2007 Last visit: 5/27/2024 Posts: 724 Rating:
shouldn't you be using the #light bit, in stead of your timer output? |
4/25/2012 10:34 AM | |
Thanks boazeventall, now I understand were your problem is. There are more than one solution for this, I will give you one: I suppose you understandyour current logic, so I dont want to change it too much to make it more difficult for you. 1. You replace your #Set time with a flag and name it for example#Start sequence. 2. You insert afirst networkand take a negative pulse from your #Set time input and setthe#Start sequence flag. Thenegativ pulse will preventtostart the sequence over and over again. 3. When you reset the#light, in parallel you also resetthe flag #Start sequence. Now your sequence is ready again. Unfortunatly I dont haveStep7 V11 installed on my PG, otherwise I would send you a picture. Regards. |