5/29/2018 2:33 PM | |
Joined: 8/31/2013 Last visit: 4/18/2024 Posts: 606 Rating: (41) |
Hello Try to make jogging to the Axes against the Limit Switch direction |
Warm Regards |
|
5/30/2018 11:21 AM | |
Joined: 10/11/2006 Last visit: 4/19/2024 Posts: 5820 Rating: (787)
|
Hello, no move command must be active. Overrun of the software limit switches If a software limit switch is crossed, technology alarm 534 is output, and the technology object is disabled (alarm response: remove enable). Retracting To retract the axis after violation of the software limit switch, follow the steps below: 1. Acknowledge the technology alarm. 2. Move the axis in the retraction direction until the software limit switch is left. If you move the axis opposite the retraction direction before the software limit switch is left, the monitoring with be triggered again. 3.2.7.3 Software limit switch https://support.industry.siemens.com/cs/ww/en/view/109749263 |
With best regards, |
|
5/30/2018 2:25 PM | |
Joined: 4/28/2015 Last visit: 1/4/2024 Posts: 36 Rating: (1) |
One question, when i do the acknowledge by MC_RESET should the MC_POWER be disabled or not? |
5/31/2018 1:55 PM | |
Joined: 4/28/2015 Last visit: 1/4/2024 Posts: 36 Rating: (1) |
The problem was the the parameter Restart, it was TRUE, changed to FALSE and it was the possible to acknowledge both HW and SW switches and the move out from the limit. |
This contribution was helpful to2 thankful Users |