Is PtP software installed on your ES? |
1/17/2012 3:29 AM | |
Joined: 9/27/2006 Last visit: 3/26/2025 Posts: 12344 Rating:
|
Hello, Guest; As stated earlier by our friend Rated-X, it sounds as if you have not parametrized the CP in your rack, so it cannot exchange with your PLCs. For that you need the serial CPs Point-to-point Parameter interface softwarte, that you can download here: Download CD "CP340, CP341, CP440, CP441" The parameter selection will depend on the protocol selected for your CP, so search for itusing the search box at the right of this page. Here is an example of settings used for a CP 340 and the 3964R protocol: Parameterizing and programming a point-to-point connection with CP340 and 3964R Protocol Hope this helps, Daniel Chartier |
1/17/2012 3:32 AM | |
Joined: 9/27/2006 Last visit: 3/26/2025 Posts: 12344 Rating:
|
Hello, Guest; As stated earlier by our friend Rated-X, it sounds as if you have not parametrized the CP in your rack, so it cannot exchange with your PLCs. For that you need the serial CPs Point-to-point Parameter interface softwarte, that you can download in the following FAQ, that applies specially to your problem: How do you download a loadable driver such as "Modbus Master (RTU)" into a CP341 that is connected to an S7-400 H system by means of an ET 200M? Hope this helps, Daniel Chartier |