Hello GAS2 Good news: Your IM151-3PN (6ES7151 3BA23-0AB0) supports MRP as of Firmware V7.0. Bad news: Your S7 319-3 CPU (6ES7 318-3EL00-0AB0) with Firmware V2.7 does NOT support MRP (I'm afraid you'll need a newer CPU and a 6ES7 318-3EL01-0AB0 as of Firmware V3.2 does support MRP). Have a look too at Which IO controllers and IO devices support the following functions: IRT, prioritized startup, MRP, MRPD, PROFIenergy, Shared device, MSI/MSO, I device, Isochronous mode, System redundancy and Option handling? for a nice complete concise list. To configure which devices are part of MRP and if they are the Manager or a Client, you click on the "PN-IO" port of each device where you'll find a Media Redundancy configuration tab.
|
Cheers |
|
This contribution was helpful to
1 thankful Users |
2/24/2016 8:07 AM | |
Joined: 10/7/2005 Last visit: 3/14/2025 Posts: 3042 Rating:
|
A switch could still help providing you can live with the fact that the CPU itself is NOT part of the MRP ring. For this to work, you use and configure two ports of the switch for the MRP ring (and make the switch the MRP Manager) and have all IM151-3's in this ring as MRP Clients (and make sure you have firmware V7.0 in them). You then use a third port of the switch and connect it via a patch lead to the CPU. |
Cheers |
|
2/25/2016 3:02 AM | |
Joined: 10/7/2005 Last visit: 3/14/2025 Posts: 3042 Rating:
|
A CP343-1 Lean (6GK7343-1CX10-0XE0) can only be used as an IO Device but NOT as an IO Controller, so it is NOT going to help you. You'd need to upgrade it to at least a CP343-1 Standard (6GK7343-1EX30-0XE0) which can be used as an IO Controller. This one though still requires a switch as the MRP Ring Manger since the CP343-1 Standard can only be a Client. As such you might as well upgrade it to a CP343-1 Advanced (6GK7343-1GX31-0EX0) which can be used as an IO Controller, supports MRP and can be the Ring Manager too. This CP costs some real money though and any usage of any 300 CP as a PN IO Controller requires additional programming effort which you need to cater for (the I/O's will now be in a DB and no longer "native" I/O's, so if your program is already done, you have a bit of rewrite to do). Personally, I'd just add a switch to your CPU and keep the none MRP capable CPU outside of the MRP ring, but the choice is yours. As for the required MRP capable IM151-3 PN V7
firmware, you'll find it HERE. |
Last edited by: fritz at: 2/26/2016 2:56:58 AMfixed up editor created formatting issue Cheers |
|
2/25/2016 10:39 AM | |
Posts: 66 Rating:
|
Thanks... I can go with managed switch only.. thanks to all again for support & guidance. |