12/4/2008 4:33 PM | |
Posts: 5822 Rating: (412)
|
Dear Darren, exchanging the Hardware first of all is a good idea. If it the problem does not move I would try to find out if there are any differences between the one link which does not work and the other links. If there is something, maybe about EMD or differing potentials. Things like that may interrupt the communication, especially if it is possible that certain changes in the System, maybe even outside the communication itself, take place. Potentials move... things like this. Have you already monitored the traffic on the RS 232 line you use? (I hopeit is a RS 232 Line you use) There arecertain monitoring tools available... maybe we could figureout some more there. Check this out: Sending and Receiving SMS Messages with S7-300/400 via serial CPs (340/341/441-2) and the GPRS/GSM Modem MD720-3 (Configuration 10) Read the chapter 8 Tips and Tricks, I think this would be very interesting. Best regards J_Bell |
5/10/2011 4:37 AM | |
Posts: 118 Rating: (4) |
Hi, We have some issue on this type of communication. Here also partner using “Telebyte Model 65A RS-232 to Current Loop Converter” same like your partner. But Ourside, we are using only CP341-1BH02 Module to communicate with them, without using any telebyte 65A convertor. first point is, do we have any option to select Active partner at CP341-1BH02 (Our SIde)? they are claiming that,they set passive transmit/receive on there side. Now the status is, other partner claiming that thy are sending heart beat on DB96.But we r not getting any heart beat on that DB96. can u give some more details on wiring between CP341-1BH02(Our Side) and Telebyte 65A Convertor(Partner Side)? The wiring diagram, what they passed us has attached. I am not able to get the clear picture with this diagram too. AttachmentTelebyte 65A - EDS Machine.pdf (122 Downloads) |
Last edited by: Maha at: 5/10/2011 5:45 AMLast edited by: Maha at: 5/10/2011 5:43 AM |
|
5/11/2011 3:10 AM | |
Posts: 95 Rating: (10) |
Hi Maha, I Found all my notes so here goes: On the L3 machines I worked on I discovered a wiring discrepancy from the factory. First check to ensure you do not have the same wiring issue on your L3 machines. On the L3, In the junction box where you connect the wiring that goes to the PLC (the terminal blocks labeled K+, K-, C+, C-) the white and black wires are switched on the back of that board. (In your attached drawing this is the rectangle labeled ‘EDS PLC I/O Box) So follow along here: If you start with the wiring at the TeleByte 65A device on the L3 machine and use the following color code according to the attached sheet: C+ = BK C- = GN K+ = RD K- = WE Then if youhook up your PLC wires to the “Master PLC Discrete” terminal blocks inside the L3 junction box using the same colors than the white and black wires are switched! It turns out that the white and black wires that were soldered to the back of the terminal blocks that come down from the TeleByte were landed on the wrong points. So that is the first thing to check. Every one of my machines had this wiring error. Regarding the RK-512 handshake, heartbeat and NAK’s. The L3 manual specified what was required at the PLC side and was followed but I could never get a stable communication between the two platforms. I believe that the TeleByte 65A is somehow corrupting the RK512 protocol but I never took the time to prove it. Since the L3 guys were not going to make any changes on their end I added a TeleByte 65A at the PLC end and changed out the CP-341 card (Part number isBelow). My thinking was I would have the L3 communicate to the TeleByte 65A via RK-512 and then the TeleByte 65A on the L3 side would communicate to another TeleByte 65A on the BHS side via RS-232 and then back to the CP-341 via RK-512. That seemed to do the trick and even though there was some expense involved in buying the additional TeleBytes, CP-341 cards and Belden connection cable everything started to work as advertised. I was told that L3 was going to be changing their manual to reflect this ‘new’ configuration but I have no idea if they ever did. Looking at your attached sheet it looks like they did. I think there were also some considerations regarding who paid for what to make the communication right but that was beyond my pay grade. The CP card I switched to is the following PN: 6ES7 341-1AH02-0AE0 Wiring on the TeleByte 65A on the L3 side (Note that this is different than the wiring in the L3 junction box for my machines as I alluded to above): C+ = BK C- = GN G = x (open) K+ = RD K- = WE Wiring in the L3 junction box (You can see how the C+ and the K- wires are reversed from the TeleByte above): C+ = WE C- = GN K+ = RD K- = BK Wiring on the TeleByte 65A on the BHS side: C+ = x (open) C- = RD G = GN + BK K+ = x (open) K- = WE The cable to connect the TeleByte on BHS side to the CP-341 card pin-out is as follows (both ends are female): DSub-9 DSub-25 1 8 2 3 3 2 4 20 5 7 6 6 7 4 8 5 9 22 The attached file contains more info and screenshots on setting up the RK512 Protocol. I hope this helps you out. It took me some time to figure it all out so hopefully you have not invested too much time and this info is just in time to save you a lot of grief and banging of heads. Best Regards, Darren Koepp AttachmentEDS - BHS RK512.pdf (121 Downloads) |
This contribution was helpful to1 thankful Users |
5/16/2011 8:44 PM | |
Posts: 118 Rating: (4) |
Hi Darren, Thanks for your kindful explanation, I was too busy with that Integration testing. So not able to check your message. Atlast we have done without changing any hardware with the reference from our very old project (10 years back one). still some more testing need to do..once done i will come back to you. The attachement how its working. AttachmentExamienr_SerialComm_Connection.pdf (119 Downloads) |
9/28/2011 11:13 AM | |
Posts: 118 Rating: (4) |
Hi Darren, Now the communication between PLC and L3 machine is working fine in normal life. [schnippschnapp] new question is splitted to while PLC going to stop mode and return back to run mode. the communication got break. |
Last edited by: O_Moderator at: 9/28/2011 12:07 PMLast edited by: Maha at: 9/28/2011 11:20 AM |
|