6/25/2021 9:10 PM | |
Joined: 9/27/2006 Last visit: 11/9/2024 Posts: 12293 Rating: (2691) |
Hello Marneuxx;
RLG:AE is a standard function used in various S5 families to scale an analog input (that is what the name AE means). It is called FB 40 with S5-155U/H CPUs, FB 250 in S5-115U... The parameters of RLG:AE will be sightly different for ecvery family of S5 CPUs, allowing for the possibilities of each. Which S5 CPU are you working with? From yur document, OGR (lower limit) and UGR (upper limit) output values for the scaled analog input is expressed in KG format, floating point value. See the screenshot below, taken from this S5-155H manual: https://adegis.com/media/asset/cda03ec307e22798906b29fe5240bd5212b24d468ea16042aacbbb3c87c9c0e5.pdf Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 06/25/2021 21:29:05 |
|
6/28/2021 6:25 PM | |
Posts: 8 Rating: (0) |
Hello Chartier, that's what I was looking for. Thanks for your help. Best reguards |