Hi! Have anyone do connection between IPC + OS + IE General + IE General + SOFNET IE RNA + SOFTNET-IE S7 REDCONNECT VM connected to LAN A and LAN B (PRP networks) and connected to S7-400H with CPU + CP443-1 RNA + CPU + CP443-1 RNA I am attaching arhitecture for better understanding. Is feasible solution? In Release notes Simatic NET V13 /"SOFTNET-IE S7 REDCONNECT VM" is written that is possible have fault tolerant connection to S7-400H with use IE General card. In Fault-tolerant Process Control Systems is mentioned PRP network only for terminal bus/not plant bus. What could be advantage of this configuration compared to classic: IPC + OS() + CP1623 +CP1623 + HARDNET S7 + REDCONNECT connected to LAN 1 and LAN 1 (2 independent network) and connected to S7-400H with CPU + CP443-1(LAN1)+ CP443-1(LAN2) + CPU + CP443-1(LAN1)+ CP443-1(LAN2) In this configuration is needed to configure 2 S7 links for exchange data between S7-300 and S7-400H?
AttachmentArhitecture_RNA.pdf (301 Downloads) |
10/2/2015 2:55 PM | |
Posts: 15 Rating:
|
Siemens help support confirmed that arhitecture is possible. IE general have to suport "Jumbo frames" which nowdays 1Gb LAN interfaces already support. |