Hi, if you connect an engineering system / HMI to ethernet, you have got ● S7 routing to the other (master) PROFIBUS interfaces (only if configured) ● S7 routing to the PROFIBUS Integrated ● S7 routing to X1400 on the CBE30 (as of V4.1 SP2) ● S7 routing between the Ethernet interfaces So that means routing for PG- and HMI functions. IP-routing from subnet to subnet is not supported. You can use an external IP router for this. (See attachment) Regards Jerry AttachmentD4x5_Routing.pdf (531 Downloads) |
Last edited by: Jerry at: 8/28/2011 5:33 PM |
|
8/28/2011 6:14 PM | |
Posts: 116 Rating:
|
Hi, yes, it is possible for STEP7/SCOUT/WinCCflex. Pls. see the boundary conditions in the attachment Prosave I don't know --- depends on the fact, it it uses S7 services. Under http://support.automation.siemens.com/WW/view/en/10347815 (Prosave download) I found no infomation about this. Regards Jerry AttachmentRouting.pdf (440 Downloads) |
9/3/2011 4:12 PM | |
Posts: 116 Rating:
|
Hi, it's not possible to select a router. For S7 routing the system get the information from the Netpro configuration. Regards Jerry |