Good Morning Has any one had a problem that they have 4 sensors that there output is only a communica protolcal that is RS485, and needs to use the inputs on the logo, I know that siemens just released Logo! CIM but it onlt takes one RS485 Sensor. Is there a way that i can connect muliple CIM or is there any other module that i can connect to the CIM so that i can connect the other sensors. Thanks Mark Paul Busuttil. |
Last edited by: MPBusuttil at: 02/16/2022 14:55:31 |
|
2/14/2022 1:33 PM | |
Joined: 12/13/2014 Last visit: 4/18/2025 Posts: 154 Rating:
|
Physically RS485 enables 32 devices on single bus, so when all sensors are set to same baud rate/parity/stop bits and with different modbus addresses (slave ID-s), then one master module can access multiple sensors. CIM manual page 63 specifies data transfer table options for MB RTU master. Another (cheaper) way is to use Logo BM 8.2 or later and Microtik Knot with IoT package, which can convert RS-485 Modbus RTU data to Modbus/TCP. |
2/21/2022 7:21 AM | |
Joined: 9/11/2014 Last visit: 4/23/2025 Posts: 832 Rating:
|
Hi, LOGO! CIM supports ModbusRTU interface. You can connect several similar sensors (RS232, RS485 or RS422) to a LOGO! CIM. The sensors are seperated by the ModbsuRTU unit-ID. |
2/22/2022 1:08 PM | |
Joined: 11/8/2018 Last visit: 4/22/2025 Posts: 107 Rating:
|
Thanks for your reply but what type of ModbsuRTU do i need to seperate them from each other? |
2/22/2022 1:35 PM | |
Joined: 9/27/2006 Last visit: 4/19/2025 Posts: 12346 Rating:
|
Hello MPBusuttil; The proposed solution (Modbus RTU over RS 485) will only work if the sensors you have can act as Modbus RTU slaves. Please statt by identifying the make and model of the selected sensors, so we can locate their operating instructions, and make sure Modbus RTU is supported. If the sensors can work as Modbus slaves, there will be no problem in connecting them to the Logo! master and collecting data from each. Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 02/22/2022 18:49:30 |
|
2/22/2022 2:12 PM | |
Joined: 11/8/2018 Last visit: 4/22/2025 Posts: 107 Rating:
|
does this help |
2/22/2022 2:13 PM | |
Joined: 11/8/2018 Last visit: 4/22/2025 Posts: 107 Rating:
|
|
2/22/2022 2:14 PM | |
Joined: 11/8/2018 Last visit: 4/22/2025 Posts: 107 Rating:
|
|
2/23/2022 2:32 PM | |
Joined: 2/22/2008 Last visit: 11/18/2024 Posts: 2698 Rating:
|
Your attachment doesn't help, these are internal descriptions on how to use modbus commands. Offer a link to your sensors with a complete instruction manual. By the way, Modbus RTU slaves need different ID numbers to work with one master. Depend on the sensors this is programmable with a PC or selectable with DIP switches. Regards, Scorp |
2/23/2022 2:43 PM | |
Joined: 8/2/2018 Last visit: 12/16/2023 Posts: 302 Rating:
|
As I remember...I need to use Logo to send data to RTU sensor for programing sensor Modbus RTU ID. In case I use more than 1 sensor that is the same model. Due to the ID will be the same on all same sensors from factory called default ID. If you use only one sensor then no need to reprogram RTU sensor ID. |