7/27/2012 9:22 AM | |
Posts: 739 Rating: (55)
|
set p0701 = 1 do an Quick commissioning (p0010 = 1) |
7/27/2012 9:55 AM | |
Posts: 16 Rating: (0) |
Hi JensS, Thanks for reply. I already try to set P701 but there is no parameter P701, after parameter P700 is r721. I thought the parameters is same as MM4?
|
7/27/2012 11:59 AM | |
Joined: 6/13/2009 Last visit: 4/16/2024 Posts: 26 Rating: (0) |
Hi, set P700=2 to enable controling from terminals. To on/off drive from Digital I/P-1 set P0840 to 722.0 Regards, Anakin |
7/27/2012 12:13 PM | |
Posts: 739 Rating: (55)
|
Then you have a new firm ware version (V4.4 or 4.5). In the near past there was a SW & HW change. Up to V4.3 is the “old world”, from V4.4 on the new. For the NEW ones: I suggest using one of the Macros (e.g. p0015 =12; or parameterise the function by using BiCo-technique - p0840 / p1113) The instruction how to do it you will find in the operating instruction chapter "7.2 Inverter control". http://support.automation.siemens.com/WW/view/en/50815575 and FAQ: http://support.automation.siemens.com/WW/view/de/51889804 |
8/8/2012 10:04 AM | |
Posts: 16 Rating: (0) |
Hi, -Thanks for reply. It have some parameters there is not available. The parameters as following: -P0015 - 1(there is no value 1 to set) -P0731 - This parameter is not available -P0842 - Not available too. - I already try all the parameters except the above parameters. Terminal 28,69,9 n 5 also I shortened, but it also not running.
|