8/2/2019 1:27 AM | |
Joined: 6/4/2008 Last visit: 4/17/2024 Posts: 1481 Rating: (322) |
Hi Andy, it may have made more sense if I'd posted this manual extract as well. I use r2094.0 to control P840. r2094.0 is the RESULT of the inversion. If You hover Your mouse over the items as per my original screenshot (Connector Binnector converter dialogue), you should note the inverter "box" appears as P2098[0].0 and the output where P840[0] is entered shows up as r2094.0 The other parameter I used in that particular project was a fault reset, and this was presented to the CU object. The parameter for S110 CU's is P2102 and this will cascade the reset via any connected Drive-Cliq components (My project was an S120 and I used P2104 which is not available in S110) Hope that clarifies somewhat.... Regards, Graeme AttachmentList Manual S110 Sheet 2468.pdf (81 Downloads) |
This contribution was helpful to1 thankful Users |