7/27/2017 6:30 AM | |
Joined: 5/12/2006 Last visit: 9/18/2024 Posts: 22364 Rating: (3011)
|
Hi, what you mean with Status 9? Regards Christoph |
7/27/2017 7:35 AM | |
Joined: 10/11/2006 Last visit: 9/18/2024 Posts: 5906 Rating: (804)
|
Hello, yes, there is a document: https://support.industry.siemens.com/cs/ww/en/view/109740023 What is the state of r2 and p10? |
With best regards, |
|
This contribution was helpful to1 thankful Users |
7/27/2017 12:04 PM | |
Posts: 36 Rating: (1) |
Hello TechTeam , 9 Staus in the Diagnostics (Missing Enable) such as : 1- OFF 1 enable missing , 2- OFF 2 enable missing, 3- OFF 3 enable missing, 4- Infeed enable missing , 5-Speed control Inhibit ... I will share a print screen as soon as possible I attached also the starter project thanks AttachmentS120_tes.zip (73 Downloads) |
Last edited by: rouk! at: 7/27/2017 12:12:06 PM |
|
7/27/2017 1:22 PM | |
Joined: 5/12/2006 Last visit: 9/18/2024 Posts: 22364 Rating: (3011)
|
R2=42 on the CU? |
This contribution was helpful to1 thankful Users |
7/27/2017 1:24 PM | |
Joined: 10/11/2006 Last visit: 9/18/2024 Posts: 5906 Rating: (804)
|
Hello, r2 = 42 at the CU? I don't know this value for a CU320.2, so if you will not get answers from other users, I would recommend to contact the customer support: Support Request : https://support.industry.siemens.com/my/ww/en/requests/#createRequest |
With best regards, |
|
This contribution was helpful to1 thankful Users |
7/27/2017 2:32 PM | |
Posts: 36 Rating: (1) |
Hello , Yes 42 on the CU 320-2DP I will recheck again , Thank you for your help !
|