5/9/2018 9:25 AM | |
Posts: 16 Rating: (0) |
Thank you for your help. It was very useful. However, how can i enable P840 parameter for infeed? changing infeed P840 directly OR connecting to input 0 of CU like drive, ... have no effect. Contactor feedback is simulated as always 1. P864 in drive is always 1 as i said before, i am commissioning based on chapter 3.6 of "s120_starter_commiss_man_1117_en-US.pdf" with some differences like telegram = 999. I attach my STARTER project as p100.ZIP AttachmentP100.zip (71 Downloads) |
Last edited by: Faryad at: 5/9/2018 9:26:27 AM |
|
5/14/2018 12:06 PM | |
Joined: 10/11/2006 Last visit: 9/18/2024 Posts: 5906 Rating: (804)
|
Hello, parameter r2=[35] of you project indicates that first commissioning was not done for the infeed. Please finish commissioning of the infeed. Please have a look on your EP-terminals of the infeed. Parameter r46.8 indicates that the EP-terminals on X21 pin 3&4 are not supplied. Because of that p840 has no effect. Provide 24V on the EP-terminal to get the SLM fully operational. You can find connection examples on section 4.9.5 of the booksize power units manual. https://support.industry.siemens.com/cs/de/de/view/109754297/en |
With best regards, |
|
This contribution was helpful to1 thankful Users |