5/24/2012 2:11 PM | |
Joined: 5/6/2010 Last visit: 8/15/2024 Posts: 89 Rating: (6) |
Can someone direct me to where it says how many VFDs I can connect to each CU320-2DP? Thank you much. |
5/24/2012 3:50 PM | |
Joined: 8/17/2010 Last visit: 8/24/2012 Posts: 26 Rating: (2) |
Maybe you try the Siemens SIZER software: http://support.automation.siemens.com/WW/view/de/54992004 It should help you getting the correct CU regards |
Last edited by: matthias000 at: 5/24/2012 3:52 PMenglish link: http://support.automation.siemens.com/WW/view/en/54992004 |
|
5/24/2012 3:52 PM | |
Joined: 5/6/2010 Last visit: 8/15/2024 Posts: 89 Rating: (6) |
That document only states the bullet points you presented. Does Siemen's provide the specifics anywhere in a document? |
5/24/2012 3:53 PM | |
Joined: 5/6/2010 Last visit: 8/15/2024 Posts: 89 Rating: (6) |
OK. I will look there. |
5/24/2012 4:48 PM | |
Posts: 58 Rating: (19) |
Dear Daynada, Please refer to the attachment. It contains two files. The pdf is extracted from pm21 catalog. It has the CU selection related information. The excel file contains my study summary from this document. Please feel free to ask any question about this selection. Regards Ajay Gupta AttachmentPages from pm21-2011-en.zip (336 Downloads) |
This contribution was helpful to1 thankful Users |
5/24/2012 5:04 PM | |
Joined: 5/6/2010 Last visit: 8/15/2024 Posts: 89 Rating: (6) |
Thank you so much. Page 12 is exactly what I was looking for. |