2/29/2012 10:16 AM | |
Joined: 10/11/2006 Last visit: 4/24/2024 Posts: 5823 Rating: (789)
|
The GSD-File "Sinamics S" is a general file and should be usable for the CU320. If you want to use the "actual" GSD File then you have to install it in Hardware Config. You can find the GSD File on your CF Card in the folder Siemens > Sinamics> Data > CFG When you have installeda GSD File orusing the"Sinamics S"File - then you should expand the veiwin the hardware catalog and insert a telegram from the list "into" the gsdFile (using drag and drop).
Orange light on the RDY LED is because the (automatic) configuration is not done yet. Orange light on the DC Link LED means you have power on your DC circuit. At this stateit is necessary to open anew starter project and configure offline a CU320 with profibus adress 12 OR just use the "search for another attendant / partner! button. Then we can go online and make an automatic configuration.
For starting wiht Sinamics S120 please take also a look on the following links: http://support.automation.siemens.com/WW/view/en/42905308(Getting Started) http://support.automation.siemens.com/WW/view/en/49084703(Commissioning with Starter) http://support.automation.siemens.com/WW/view/en/20208582(further links for applications and tools) With best regards |