Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
Actual you should have post this in SINAMICS product conference where you could get much faster & detail answer. BTW after commissioning of drive have you saved parameters from RAM to ROM? Please check the value of p0977. To save the drive object parameters, after commissioning set p0971 = 1. This will save only adjustable parameters in non volatile memory. Please refer attached sheet for more detail information. |
Last edited by: PISCEAN 2010 at: 8/25/2018 1:38:43 PM |
|
This contribution was helpful to1 thankful Users |
9/22/2018 12:07 PM | |
Joined: 11/16/2016 Last visit: 1/31/2023 Posts: 20 Rating: (0) |
Dear Experts, S120 Drive Cabinet type module Details of S120 Drive Cabinet type module: Having 2 Contol unit,1 ALM and 5 motor module. 1.) Control unit_1 having -2 motor module i.e 1 &2. 2.) Control unit_3 having -3 motor module i.e 3,4 &5. Problem: Drives parameter was lost automatically after sometimes. It was found that CU_1 all parameter was factory reset and both motor module went to quick commissioning and one of its motor module removed from its configuration. CU_2 only motor module 5 went to quick commissioning mode. I have attached the both backup i.e problematic and correct one.Please reply ASAP regards Aplaud
Attachmentproblem.zip (98 Downloads) |
9/25/2018 10:38 AM | |
Joined: 11/16/2016 Last visit: 1/31/2023 Posts: 20 Rating: (0) |
PlSCEAN 2010 Please help me problem i had entered. |