3/14/2016 10:13 AM | |
Joined: 6/29/2012 Last visit: 12/25/2023 Posts: 975 Rating: (8) |
We have CU320-2 FW4.7 connected to S7 400 by profinet for standard communication and to S7 315F by same profinet network for safety communication. So the drives are configured as shared device. The drives are working, safety by profisafe (315F) is working. But sometimes when we power everything off and on again we get fault F1611 (defect in a monitoring channel) (detail fault : 1611). We are not able to reset this error. Included are screenshots of the fault and configuration. The proposed remedy for the fault in the help seems not necessary, the settings are already ok. What could be the other reasons for this faults, and why can't we reset the fault. The internal event acknowledge bit in the telegram is set high when we reset, this should not be the problem. If power is put on plc and drives, there may be differences in startup time of drives and plc's, but that should not be a reason for not being able to reset faults. Apart from this sporadic problem, the configuration is working ok. AttachmentFlt1611.zip (114 Downloads) |
6/3/2020 4:34 PM | |
Joined: 12/19/2019 Last visit: 11/24/2022 Posts: 1 Rating: (0) |
Dear, I'm having the same problem with a 15xxF plc. Was there a solution? Thx in advance, TG |