3/25/2017 1:57 PM | |
Posts: 7 Rating: (0) |
Hellow i have Repeated problem for S120 drive each time starting the drive it trippes gving faults F7802 and F30027 together , once we resset and start again it start normally without any problems, Note : before reset the fault the DC voltage is exist on AOP : 955 VDC So can you tell me what is the problem and how to clear it Thanks ------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 3/27/2017 4:26:20 PMNew subject after splitting |
|
4/7/2017 11:26 AM | |
Posts: 7 Rating: (0) |
Thank you very much it was just as you explained and the problem solved |