3/17/2018 9:23 PM | |
Posts: 33 Rating:
Dear expert I have prob in our sys s120 2 drive from 14 drive s120 giving alarm every times falut 1600 and1611 Can you explan steps to solve thise prob ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 3/19/2018 12:50:27 PMNew subject after splitting |
3/18/2018 6:21 PM | |
Posts: 33 Rating:
I have prob in our sys s120 2 drive from 14 drive s120 giving alarm every times falut 1600 and1611 Can you explan steps to solve thise prob |
3/19/2018 2:30 PM | |
Joined: 9/8/2011 Last visit: 1/9/2023 Posts: 481 Rating:
When STO is off the drive confirms the wires are not shorted. Also, When setting up STO in Starter it defaults to confirm every 8 hours.... AttachmentSiemensDriveFaults.pdf (707 Downloads) |
A smart person learns from their mistakes |
3/19/2018 6:09 PM | |
Joined: 10/11/2006 Last visit: 1/27/2023 Posts: 5404 Rating:
Hello, If you don`t have STARTER/SCOUT/TIA you can also have a look at parameter r945 and r949 where you can find the fault 01611 and in the corresponding index of the second parameter the fault value. You can find detailed information about fault cause of the different fault values in the list manual of the S120. or in the drive faults pdf of KFoldesi. |
With best regards, |
