1/11/2021 3:22 PM | |
Joined: 10/11/2006 Last visit: 1/30/2023 Posts: 5407 Rating:
Hello, check the conditions for torque limiting and the settings in the command. Referce value in drive P2003 and at the TO must be the same. Requirements for force/torque limiting ● The technology object and the reference torque of the drive have been configured correctly. ● No errors that prevent enabling are pending for the technology object (the technology object must not be enabled). ● The drive must support force/torque reduction. Only PROFIdrive drives with SIEMENS telegram 10x support force/torque limiting. ● Interconnection in the SINAMICS drive: – P1522 to a fixed value of 100 % – P1523 to a fixed value of -100% (e.g. through interconnection to fixed value parameter P2902[i]). – P2194 Threshold value for the parameter "InLimitation" must be < 100% (default 90% 7.15.3 MC_TorqueLimiting V5 (S7-1500, S7-1500T) https://support.industry.siemens.com/cs/ww/en/view/109766462 |
With best regards, |
1/11/2021 3:30 PM | |
Joined: 1/20/2020 Last visit: 1/13/2023 Posts: 4 Rating:
ok Thx |