4/24/2012 2:10 PM | |
Posts: 5 Rating: (0) |
Hello I wonder if it is possible to supply a 5kW SLM and a 11kW Blocksize motormodules on a 525VAC supply. Best Regards Jonas |
4/25/2012 12:06 PM | |
Posts: 58 Rating: (19) |
Dear Jonas, You can use a SLM 5kW on 525VAC (which is 480V +10%, the maximum limit). But when commissioning the SLM you have to enter 480V in p210, you cannot enter a value greater than 480V. It is recommended to use these units till 480V only.!!!!! I was not able to find a motor module 11kW anywhere. Can you please provide the MLFB ? As also the motor must be able to sustain a PWM voltage with normal value of approx 700V (525V x 1.35). Please refer to the attached extract from the list manual. Regards Ajay Gupta Attachmentp0210_SLM.pdf (149 Downloads) |
6/17/2016 11:25 AM | |
Joined: 8/21/2014 Last visit: 9/19/2024 Posts: 1024 Rating: (14) |
New question published by kiran1384 is split to a separate thread with the subject INFEED MODULE: What to set in p210?. Best regards |
My Forum is the place to personalize your profile, |
|