7/28/2015 5:51 PM | |
Posts: 87 Rating: (6) |
Hi everybody. I have this devices: CU320-2PN (6SL3040-1MA01-0AA0) firmware V4.70 BLM 6SL3130 1TE22 0AA0 MOMO 6SL3120 1TE15 OAA4 MOMO 6SL3120 1TE21 OAA4 IM151-8 PN/DP CPU (6ES7 151-8AB01-0AB0) firmware V3.2 TIA V13 SP1 Update 2 I am trying to do a Profinet connection between s120 and IM151-8. I configured the hardware from sinamics s120 at devices and networks (changed the Profinet Name and IP AddresS) and I also configured the drives objects. (I am using EPOS with telegram 111). When I go on Accessible devices, the hardware is found (Name and IP address are correct) but it changes a Sinamics S120 for a Sinamics G130 / G150 and I can not stablish a communication between s120 and the IM151-8. I saw examples of applications by Siemens only settings between s120 and plc 1200 and 1500 on the TIA Portal, and examples of applications between s120 and plc S7300/400 on the Step 7 V5., both applications in EPOS mode. The sinamics s120 it is avaliable for work in EPOS mode with an IM151-8 PN/DP CPU on the TIA Portal? AttachmentS120_to_G130.pdf (124 Downloads) |
7/28/2015 7:42 PM | |
Posts: 87 Rating: (6) |
Hi Christophd. For the drive side i'm using Starter V4.4.0.3 In the attachment there are the screenshot that you want. regards. AttachmentConfiguration.rar (132 Downloads) |