7/18/2014 12:14 AM | |
Posts: 5 Rating: (0) |
Dear Experts Im working with a S120 (CU320-2PN), SLM 5KW and Double Motor Module. I did all the steps for the online comissioning and that stuff. I have in my starter the CU, the two Servo (double motor module) and some configuration for my wiring. I have some doubts. 1- Who controls the Line Contactor? Im using my DO 8 from the CU320 to energice the Line Contactor,but when I try to do the interconnection in the Input/output screen, it ask me to select the device and I dont have a infeed configuration in the starter. Should I select Servo 1 or Servo 2? 2- The same for the Contactor Feedback, Im using my DI 9, should I select servo 1 or servo 2? 3- And the most important. The signal EP for the SLM 5KW, one manual (attach 1 "manual 1") tells me to conect the EP signal to an aux contact for the Main Disconnecter, directly to the 24VDC from a Power Supply... Another manual (attach 1 "manual 2", same PDF) tells me to connect the EP signal to the same aux contact, but that signal should come from a DO of the CU320, but it doesnt say the configuration for the DO. The two manuals are from 01/2011 date. Which configuration is the right one. Please Help. Thanks Javier
AttachmentManuals.pdf (67 Downloads) |