1/15/2019 7:58 AM | |
Posts: 18 Rating: (0) |
Ahhh :) So then i´ll start with installing V15 then :) Wiiring is as follows-- P1 on the drive to P1 on the PLC //Jim |
1/15/2019 9:01 AM | |
Joined: 2/7/2018 Last visit: 3/14/2023 Posts: 181 Rating: (30)
|
Hello, The SINAMICS S210 is fully integrated in the TIA Version V15.1 and SINAMICS S210 FW V5.2. TIA Version V15.1 is already released (see link below) and SINAMICS S210 FW V5.2 will be released in the next days. For all SINAMICS S210 FW Version < V5.2 the SINAMICS S210 needs to be implemented by GSD-Files. The drive optimization and safety-commissioning can be done via the Webserver. At the first time you need to go online via the X127 commissioning interface. The X127 has a default IP-Address of 169.254.11.22 / Subnetmask 255.255.0.0 Further information about the Webserver can be found in the S210/1FK2 operation manual, Chapter 6 “Commissioning and diagnostics using the web server”, pdf-page 179. SINAMICS S210/1FK2 Operation Manual Additional Links: Delivery release TIA Portal V15.1 For which controllers is the SINAMICS S210 servo drive system configured? Best Regards, |
1/17/2019 2:03 PM | |
Joined: 5/12/2006 Last visit: 12/20/2024 Posts: 22482 Rating: (3039)
|
Hello, on which port of PLC you pc is connected? Do you have any screen?
Christoph |
1/17/2019 3:05 PM | |
Posts: 18 Rating: (0) |
Yes i have tried that aswelll |