Dear all I have plc S5 130K and need to upload its software by using PG 740. Please help me if possible or no
---------------------------------------------------------------------------------------------------- |
Last edited by: Min_Moderator at: 7/30/2015 10:00:29 AMNew subject after splitting |
|
8/27/2015 8:07 AM | |
Joined: 11/10/2010 Last visit: 5/27/2023 Posts: 15 Rating:
|
Hi pg740 has a builtin tty port refer the manual not required to buy any external tty converter
|
8/27/2015 11:18 AM | |
Joined: 10/7/2005 Last visit: 5/29/2023 Posts: 2965 Rating:
|
Hello ABD2008 sorry, you can NOT use a PG740 to upload from a S5 130k. You need a PG675 (or older) and CP/M Step 5 to do so and the links below have all the gory details on what to do and look for for: https://support.industry.siemens.com/cs/document/2205332/upgrading-from-controllers-s5-110a-and-s5-130ak-to-controllers-s5-115u-and-s5-135u https://support.industry.siemens.com/cs/document/217845/how-do-you-connect-a-pg-6xx-and-a-pg-7xx https://support.industry.siemens.com/cs/document/188113/where-can-you-hire-the-pg631-programming-device-to-program-the-simatic-s5-automation-devices-s5-110a-and-s5-130ak I hope this helps and good luck |