11/29/2018 4:19 PM | |
Joined: 12/18/2014 Last visit: 9/23/2024 Posts: 33822 Rating: (4203) |
It is better if the original STEP5 program is available. |
11/29/2018 4:51 PM | |
Joined: 12/18/2014 Last visit: 9/23/2024 Posts: 33822 Rating: (4203) |
That was the reason for my first answer ... |
11/29/2018 4:57 PM | |
Joined: 1/25/2016 Last visit: 9/23/2024 Posts: 14 Rating: (0) |
Here you go. Thank you.
AttachmentS5 PLC program.zip (299 Downloads) |
11/29/2018 5:05 PM | |
Joined: 12/18/2014 Last visit: 9/23/2024 Posts: 33822 Rating: (4203) |
Do you know, which S5 type you have? S5-115U? Or S5-135U? Or other? |
11/29/2018 5:24 PM | |
Joined: 1/25/2016 Last visit: 9/23/2024 Posts: 14 Rating: (0) |
I just checked the picture from the project. It is an 115U |
This contribution was helpful to1 thankful Users |
11/29/2018 6:08 PM | |
Joined: 12/18/2014 Last visit: 9/23/2024 Posts: 33822 Rating: (4203) |
I insert the FBs (FB250 and FB251) in your program. This FBs are FB in firmware of the PLC. FB250 = Reading and Scaling an Analog Value. This are Standard-FBs from Siemens and can't convert to S7. AttachmentKALKLO.zip (322 Downloads) |
11/29/2018 6:11 PM | |
Joined: 12/18/2014 Last visit: 9/23/2024 Posts: 33822 Rating: (4203) |
I you don't have to manual you can download from here: S5-115U Programmable Controller Take a look at chapter 10.9 (PDF page 362). |
11/29/2018 7:39 PM | |
Joined: 12/18/2014 Last visit: 9/23/2024 Posts: 33822 Rating: (4203) |
Better, you use the S7 scale and unscale funktion. How can you standardize and destandardize analog values with STEP 7 V5.5? How do you standardize and destandardize analog values with STEP 7 (TIA Portal)? |
11/29/2018 8:28 PM | |
Joined: 1/25/2016 Last visit: 9/23/2024 Posts: 14 Rating: (0) |
Yes that was also what i figured out. And now i have the HI and LO limit. Thank you so much for your help. |
11/29/2018 8:35 PM | |
Joined: 12/18/2014 Last visit: 9/23/2024 Posts: 33822 Rating: (4203) |
You're welcome. I hope you can finish your project successfully. |