10/8/2009 12:56 PM | |
Joined: 9/27/2007 Last visit: 4/25/2023 Posts: 36 Rating:
|
I want to migrate S5 to S7 without exchange S5 remote IO's I attached S5 configuration in this post please tell me how I can do with best and inexpensive solution I know that i can with IM 463-2 and IM 314 but i don't know how i can do this with profibus solution and so I can't find order No of cable connaction between IM 463-2 and Im 314 please help me for "profibus solution" and "cable order no" as soon as possible AttachmentS5_S7.pdf (76 Downloads) |
Last edited by: Rasool S.Alizadeh at: 10/8/2009 1:20 PM |
|
10/8/2009 3:48 PM | |
Joined: 9/27/2006 Last visit: 5/30/2023 Posts: 12025 Rating:
|
Hello Rasool; The Profibus solution for S5 CPUs uses a IM 308C in conjunction with the configuation software "ComProfibus"; Siemens refered to this as a ET 200U Profibus slave. As Siemens has discontinued the production of S5 modules, this will be an expensive solution. Have a look at one provider found on the web (there are others, search for them): http://www.lpc-uk.com/siemens/profi/main.htm As for the cables for the IM 463-2,refer tochapter 7of the manual "S7-400 Module data" http://support.automation.siemens.com/WW/view/en/1117740 It discusses the use of an IM 463-2 connected to IM 314s. They refer to the cables generically as "721 cables" and they give the pinouts for the cable and the terminating connector required (luckily, as they are also no longer manufactured). Hope this helps, Daniel Chartier |