Hi blueberry. Thereare several options to do so, please check this links: WinCC and S5 in the forum WinCC and S5 in the FAQ's You will find several Aplication notes and tips, depending on the hardware you have right now you should choose the bes aplication for you. Have nice day. |
Keep working! |
|
7/16/2009 7:28 AM | |||||||||||||||
Joined: 9/27/2006 Last visit: 6/5/2023 Posts: 12034 Rating:
|
Hello blueberry; I have looked through all my WinCC configuration manuals, and confirmed that no version I have worked with has a driver for Sinec L1. For example, here are the drivers you can use with a S5-115H:
http://www.industry.siemens.de/industrial-services/EN/solution_services/simatic_addons/proto_L1.htm You could think about setting up a S7-300 CPU (with CP 341) as a data concentrator to the S5 network (send/recieve interfaces can be setup for master/slave and slave/slave configurations), and then connect the S7-300 CPUto WinCC through the S7 protocol suite channel(MPI, Profibus, Induistrial Ethernet). This might help you solve your problem, although there will be some expenses and work. Hope this helps, Daniel Chartier |
||||||||||||||
10/19/2011 2:01 PM | |
Posts: 3093 Rating:
|
Just for the sake of completeness: this driver was discontinued and is not longer available. Regards, Kaulquappe |