5/4/2011 12:48 PM | |
Posts: 2 Rating: (0) |
Hello, I am very new to S7 PLC and need help urgently cos boss require answer and action immediately. I need to know the correct syntax for writing the time of 100 secs because one of our interlock logic will activate in 100 secs. Existing format now is S5T#1M40S but after reading thru the manual, I suspect this form is wrong. We encountered a fault that will activate this logic sequence in 100 secs but did not happen. I check the timer and now suspect the syntax is wrong maybe...Can someone help out here now? Should it be written as: 1. S5T#1M_40S 2. S5T#0H_1M_40S Pls help me out as I need to change this PLC program. AttachmentNW3_Strand Monitor.pdf (146 Downloads) |
This contribution was helpful to1 thankful Users |
5/4/2011 12:59 PM | |
Posts: 8946 Rating: (999) |
Writing S5T#1M40S is OK. The error must be somewhere else. |
This contribution was helpful to1 thankful Users |
5/4/2011 1:18 PM | |
Joined: 1/28/2009 Last visit: 9/10/2024 Posts: 6849 Rating: (1365) |
Hi Please check the following documents to get the basic information on STEP7 Working with STEP 7 Getting Started and complementary data here: SIMATIC Programming with STEP 7 V5.5 or Programming with STEP 7 V5.4 regards |
This contribution was helpful to1 thankful Users |