Hello Vega, |
5/21/2014 8:10 AM | |
Posts: 107 Rating:
|
For CP343-1 Lean You Must use AG_SEND function and for s7-1200 You must use TCON+TRCV function.The communication protocol Must be ISO on TCP. i Think This Example Project will help.I had Same Problem But now It's Worked. AttachmentCP343-1 Lean_S7-1200.zip (372 Downloads) |