Hello Habela; I agree with IBN-Service that a BMS has to comply to many standards that are not covered by the S7-1200 at this time. You need FailSafe blocks, ESD logic and you mustmeet NFPA requiurements. To give you an idea of what you would need to implement have a look at the following information: First, a Siemens BMS proposal: This is how the product is introduced: • Pre-packaged designs optimally scaled to fit your fired equipment process • Pre-assembled NEMA cabinet integrated with TÜV-certified PCS 7 hardware and software • Industry compliant to NFPA 85 and 86, IEC 61511 and 61508, and ANSI/ISA 84 standards • Pre-configured and TÜV-certified BMS engineering templates To compare offerings, see this PPT presentation from a competitor system Burner Management System - Preferred Instruments Each Burner Management System should be designed in accordance with the below listed guidelines to control and monitor all sequences of the start-up and shutdown of the burner -National Fire Protection Association (NFPA 8501 /8502 or others) -Industrial Risk Insurers (IRI) -Factory Mutual loss prevention guidelines Each burner management system should be designed to accomplish a safety shutdown inthe event of an unsafe condition.Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 8/19/2013 9:30 PM |
|
This contribution was helpful to3 thankful Users |
8/18/2013 4:22 PM | |
Joined: 11/1/2007 Last visit: 5/22/2024 Posts: 36 Rating: (0) |
Can I use it as a partial part only of the burner management system reducing the number of relays on the hardwire? |
8/22/2013 10:21 PM | |
Joined: 11/1/2007 Last visit: 5/22/2024 Posts: 36 Rating: (0) |
Thank you so much for the great help |
Follow us on