Hello szyroki, should be possible, just double check on the S5 about the RS-422 interface. Some S5 are using TTY (20mA current loop) interface which is not supported by your CM. Best Regards. |
Give us your feedback and show us your respect! |
|
6/13/2014 8:47 AM | |
Joined: 12/1/2009 Last visit: 2/9/2025 Posts: 672 Rating:
|
Sorry my friend szyroki , its always better to take a look intothe documentation. So the manual for the CM PtP is only talking about S7-1500. I am afraid that in combination with a S7-1200it is not going towork. Last time I connected to S5/TTY/3964(R) was with S7-300 through CP341. Best Regards. |