8/6/2019 12:46 PM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating: (1051)
|
okay... you can reach other PLC with accessible devices, but you can not reach this PLC. so you can only try to act with SMC. Try to load your project to the card and then start the CPU with the card. SIMATIC S7 S7-1200 Programmable controller maybe a FW-Update with Memory-Card helps: hope this helps, regards, |
FCK WAR! |
|
8/6/2019 1:24 PM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating: (1051)
|
hi, which SD-Card do you have? is it a Simatic Memory Card? regards, |
FCK WAR! |
|
This contribution was helpful to1 thankful Users |
8/6/2019 1:39 PM | |
Joined: 7/9/2015 Last visit: 5/29/2024 Posts: 3850 Rating: (564)
|
Hi, yes of course, there is a difference! I still asked you some posts before - please read... You need a card like this: https://support.industry.siemens.com/cs/de/de/pv/6ES7954-8LC03-0AA0/pi?dl=de Regards, Towome |
Last edited by: Towome at: 08/06/2019 13:40:10
|
|
8/6/2019 1:45 PM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating: (1051)
|
hi, it is also described in the manual more than one time that you need a Simatic Memory Card. SIMATIC S7 S7-1200 Programmable controller - Using a memory card |
FCK WAR! |
|
Follow us on