Solved! Thanks Galen. "The CPU has not supported that option for LED since the 02 versions. The control of the Link LED was moved to the port hardware and is no longer under CPU control." Used the Profinet Library with instruction called, LPNDR_ReadGlobalInfo. Key for this was to execute the block using a clock bit, and also having it point at Profinet_1 not the individual ports. Having the DataRecord point to the array [1..2] of "LPNDR_typePortLinkState", not [0..1]. I receive a 1 when linked, and a 2 when not. See image attached. |