1/27/2015 10:26 AM | |
Joined: 5/29/2013 Last visit: 10/22/2024 Posts: 29 Rating:
|
Hi, I am constantly using S7 CB 1241 (RS485) Modbus comms to field devices, but this one was designed as a custom device. However I can see it with PC using Modbus Poll program. Also I can see other devices - that means, that wiring is ok. Problem appears when I just move wires to PLC, I still can see other devices get response, but from this device I get errors. picture 1) Initial setting reccomended from supplier and example. 9600 8n1 node 1 picture2) What do I see in Modbus Poll program on the PC picture3) Modbus Poll configuration on the PC picture4) MB_MASTER instruction in S7 Every time when MB_MASTER contacts node one, it gets error 8383, which means "Error in the data address or address outside the valid range of DATA_PTR" If somebody could help me with translating this Raw Data Poll: 01 - node number 03 - function code 00X20 - register DEC 32 (is it 40032 or 400032 for function code 03?) 00 09 - quantity of registers (also tried with 1 word only and 1 dword) 84 06 - CRC16 - I am not sure if MB_MASTER instruction sends it automatically.. I need to get at least one word of feedback, then I can manage.
Attachmentmodbus setup.pdf (343 Downloads) |
1/27/2015 4:03 PM | |
Posts: 1058 Rating:
|
Hello frzw, same topic has been discussed here: Modbus ,Error status ( MB_MASTER ) 8200,8383 regards |