3/3/2014 11:34 AM | |
Joined: 1/17/2007 Last visit: 3/10/2025 Posts: 1557 Rating:
|
There is no function to read a 4-word value. You will have to read it using to 2-word values and recombine these back into your 4-word value at the receiving end. Is the 4-word value a real (floating point) value? If so, you would be advised to read this thread. /tf/WW/en/Posts/104581 |
Programming today is the race between software engineers building bigger and better idiot proof programs, and the universe producing bigger and better idiots. |
|
4/12/2014 3:44 PM | |
Posts: 150 Rating:
|
Please find attached a full working copy of a S7-1200 reading 3 PAC3200 Sentrons. The S7-1200 is also reading 4 word registers using LReal data type as mentioned in a previous post. AttachmentPAC3200.pdf (1603 Downloads) |
Last edited by: Nikzitronik at: 4/12/2014 4:24 PMI cant :) Last edited by: Nikzitronik at: 4/12/2014 4:23 PMI can find a way to post the V12 Archive file as it is over 3MB. If you know a way to upload please let me know it. In the mean time I attached program printout |
|
This contribution was helpful to
1 thankful Users |
1/26/2016 2:38 PM | |
Posts: 6 Rating:
|
Hi, I read 2801 is 32 bit, 801 is 64 bit. |
5/11/2016 2:09 PM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4766 Rating:
|
New question published by ingant is split to a separate thread with the subject Read the active power by a PAC3200. Best regards |
8/26/2016 12:01 PM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4766 Rating:
|
New question published by joemaria is split to a separate thread with the subject SENTRON PAC3200, convert the 4 word parameter energy to a floating value of 32 bits. Best regards |
1/19/2017 2:52 PM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4766 Rating:
|
New question published by vrk is split to a separate thread with the subject Sample program to communicate s7 1200 cpu and pac3200 through modbus tcp. Best regards |