Hello, there is a description about the configuration: 2.2.2 Automatic transfer of drive and encoder parameters in the device For operation, identical reference values for the drive and encoder connections must be set in the controller and in the drive and encoder. The speed setpoint NSET and the actual speed value NACT are transferred in the PROFIdrive telegram as a percentage of the reference speed. The reference value for the speed must be set identically in the controller and in the drive. The resolution of the actual value in the PROFIdrive telegram must likewise be set identically in the controller and in the drive and encoder modules 2.2.5 Data connection PROFIdrive drive/PROFIdrive encoder The data connection of PROFIdrive drives and PROFIdrive encoders occurs either directly via the PROFIdrive telegram or via a data block. Use the connection via data block if you want to influence or evaluate telegram contents in the user program for process-specific reasons. https://support.industry.siemens.com/cs/ww/en/view/109773400 |