11/29/2012 5:51 PM | |
Posts: 5 Rating: (0) |
The TIA software is expecting V2.2 the plc has 2.2.0 according to the online access tool
|
11/30/2012 7:38 PM | |
Joined: 7/7/2010 Last visit: 11/11/2024 Posts: 15389 Rating: (2443)
|
Since your PLCs have FW 3.0, you will need to change the plc in your project(s) to reflect this FW version (the S7-1211 is only available in FW3.0). Once you do that, you should be able to download. If your portal does not show FW3.0 as an option, download & install the hardware support pack #0026. (HSP 26). If it is still not compatible, it would be best to contact Siemens via Support Request to help correct the problem. |
science guy |
|
10/6/2013 2:58 PM | |
Posts: 2 Rating: (0) |
I get the problem same with you. Can you give me solution step by step. My PLC can't online. Please help me |