8/6/2009 4:07 PM | |
Joined: 11/26/2008 Last visit: 12/8/2023 Posts: 101 Rating:
|
Torunyusuf, There may be some information of interest in the attached file... AttachmentCommunication_S7-1200_to_S7-300_en.zip (2710 Downloads) |
8/6/2009 6:21 PM | |
Posts: 12 Rating:
|
Hi Abyrne, Thank you verymuch your answer. it's helpfull. i can not find them. BEST reagards yusuf torun |
8/7/2009 2:22 PM | |
Posts: 60 Rating:
|
Hi torunyusuf, For the S7-1200, I've done it both ways. Using tcon/tsend/tdiscon and tsend_c. I've not used Netpro to parameterize my connections for T-communications, only for Get/Put type so I cannot offer any help. For my S7-300/400 side, I followed the steps outlines in the document "System Software for S7-300/400 System and Standard Functions - Volume 2/2 A5E00739858-01". When configuring UDT65 which contains the connection information, I used S7-400 as my partner since there is no support in Step7 Classic for the S7-1200. This document can be found here: http://support.automation.siemens.com/WW/view/en/1214574 You might also look at the Open Communication Wizard, it assists Step 7 Classic in parameterizing your UDT65 correctly. I'm sorry, but I cannot seem to find the link to it right now. I'll re-edit this post later if I find it again. One hint...beware of endians, this will bite you. The S7-300 and the S7-1200 have different endianess which can be a pain when defining IP address and TSAPs. |
Last edited by: Zunar at: 8/7/2009 2:25 PMAdded some more info, fixed some typo''''s |
|
12/3/2009 12:10 PM | |
Joined: 9/28/2005 Last visit: 12/10/2024 Posts: 2957 Rating:
|
Hi all, In addition to all said here I can post one link. This is all you need I think. Look here. |
Best regards, |
|