Hello, which version has your modul CM1243-5. See the informations from the FAQ: http://support.automation.siemens.com/WW/view/de/57989692 With best regards |
4/17/2012 1:45 PM | |
Posts: 4 Rating:
|
Hi, solved theproblem. I have aCM1243-5v1.1. The problem wasin theTIA, becauseI did not havethe appropriateGSD. Here is the linkto the appropriateGSD: S120CU310FW2.6 - <link>http://support.automation.siemens.com/WW/llisapi.dll/csfetch/49216293/S120_V2_6_SI2280E5.zip?func=cslib.csFetch&nodeid=49588500</link> The GSDmust be installedin theTIAthatwasoversellconnect both. Providesa helpfulpdf: <link>https://a248.e.akamai.net/cache.automation.siemens.com/dnl/TQ/TQ1MTg5AAAA_56749384_Tools/56749384_SINAMICS_G120C_at_S7-1200_DOKU_v10_en.pdf</link>
Thank you for your help:) I considerthe subjectclosed. |
Last edited by: Jacekk at: 4/17/2012 1:48 PM |
|