8/29/2015 6:55 AM | |
Joined: 10/28/2014 Last visit: 3/6/2024 Posts: 21 Rating: (0) |
Dear Friends ! I am using siemens analog input module 6ES7231-4HD32-0XB0 for S71200 PLC, to connect with 2 wire configured transmitter. When I check the analog channels I don't get 24VDC, and my transmitter is not work. Is the module doesn't support 2 wire system? shall I need 4 wire system ? or my wiring is wrong? Here is I attached my wiring diagram and siemens corresponding manual. Thanks, Attachmentanalog module wiring configuration.pdf (855 Downloads) |
8/29/2015 7:07 AM | |
Posts: 1529 Rating: (202) |
Did you connect the +24V and M to the SM? It is missing in your drawing. |
8/29/2015 7:23 AM | |
Joined: 10/28/2014 Last visit: 3/6/2024 Posts: 21 Rating: (0) |
Yes sir it was connected, missing in the drawing only. |
Follow us on