1/18/2013 3:47 PM | |
Joined: 7/7/2010 Last visit: 2/7/2025 Posts: 15619 Rating:
|
Hamid, The S7-1200 will not respond to requests from remote devices for symbolic addressed DBs regardless of how well we guess their internal structure. It simply refuses the request. It does not try to give you what you want, or even what the plc may 'think' you want. It just refuses. automat_plc, That said, there should be a way to get the symbolic tags from a named db (rather than by number) provided they were created with the 'visible' flag checked. For example, the hmi can read/write symbolic tags if they are set as visible. The web server (if so configured and enabled), can access db_by_name.tag_by_name. So, with the name of the db and name of the tag, the scada system may not be able to access the data, but anhmi project might. If the internal web server is enabled, you can craft a web scraper to read the value periodically and pass it to your scada system. |
science guy |
|
1/18/2013 4:11 PM | |
Posts: 6 Rating:
|
Very interesting ... thanks!! I'll think about this opportunity. Best regards ... |
1/18/2013 4:18 PM | |
Joined: 1/28/2009 Last visit: 1/30/2025 Posts: 6859 Rating:
|
Dear huggy_d1, While speaking about reconstructing a DB with absolute addresses based on the symbolic names and their orders, I do not think CPU refuses a valid absolute addresses inside a existing DB.The possible problems may be non existing cells or wrong guessing addresses corresponds to given symbol. It is a possible way but I rephrase it again ,It may not lead to a perfect result. Many regards from Hamid Hosseini |