1/16/2017 8:52 PM | |
Joined: 5/12/2006 Last visit: 9/24/2024 Posts: 22370 Rating: (3012)
|
Hello, tehj project on the PLC was created and loaded with V13.0.0.x, and the TON Block is version depended. You must upload the config to a V13.0.0.x project insteed a V13.0.1.x project. For this open a V13.0.0.x project in compatibility mode and upload the device. https://support.industry.siemens.com/cs/ww/en/view/82169157 |
1/16/2017 9:12 PM | |
Joined: 12/25/2016 Last visit: 7/10/2024 Posts: 90 Rating: (0) |
thank you sir. i will try it tomorrow. |