Hello perhaps this one helps: https://support.industry.siemens.com/cs/ww/en/view/20982954 Bye Murof |
If this Information really helps, you could use the Rate function |
|
1/1/2019 3:04 PM | |
Joined: 6/8/2009 Last visit: 9/21/2023 Posts: 9 Rating:
|
Hi everyone Data transfer to S7400 CP 443-1 by S7-1200 Plc has been successfully completed. What is important here is that the rack number and slot 0/3 must be entered. Also the connection must be hex 03. Best regards AttachmentPutGet_from1200_to_400CP443_1.zip (395 Downloads) |
This contribution was helpful to
1 thankful Users |
10/10/2020 10:29 PM | |
Joined: 6/8/2009 Last visit: 9/21/2023 Posts: 9 Rating:
|
Hi Patil P ; Picture will be helpful. |