5/27/2013 4:48 PM | |
Posts: 215 Rating: (6) |
Hello MadsDK, please look up the s7-1200-manual http://support.automation.siemens.com/WW/view/de/36932465 for "HSC" Also look up the help of TIA portalfor the expression"HSC". You will also get some information regarding configuration. For programming: while programming a block you will see at the right collumn the chapter "technology". Click on "Counting" and the function "CRTL_HSC" shows up. maybe you will find some similar postings in this forum like this: /tf/WW/en/Posts/89664 Did this get you closer solving the problem? Regards |
This contribution was helpful to1 thankful Users |
5/27/2013 4:48 PM | |
Posts: 5225 Rating: (1185) |
Hi Mads, Hope I can help you with the attached PDF.. It is a step by step for setting the system to give you a frequency read from ID1000. Let us know if this helps. PS: "Quick & Dirty" because no words are wasted in the step-by-step explaination. AttachmentQuick & Dirty_HSC for frequency indicator.pdf (2842 Downloads) |
This contribution was helpful to3 thankful Users |
5/27/2013 5:15 PM | |
Posts: 4 Rating: (0) |
Thanks I got my HSC working but how do I get the value from the HSC to a speed value a m/s? Again thanks |
This contribution was helpful to1 thankful Users |
5/27/2014 3:16 PM | |
Joined: 9/1/2005 Last visit: 3/5/2024 Posts: 4097 Rating: (193) |
New question splitted to modbus device to read the engine hours. Best regards CS Moderator |
My Forum is the place to personalize your profile, |
|
This contribution was helpful to1 thankful Users |